No Tags Found!

dipil
713

Dear Shailesh If its possible post the photos of the arragement made for earthing of tankers... That will be very usefull... Regards, Dipil Kumar V
From India
Kesava Pillai
252

Dear Abhay,
Your using an iron rod is of no use, and not acceptable.
Having a meter of copper earthing rod of half inch dia, driven at least half a meter deep into the ground with undisturbed soil if well wetted will normally meet the requirement in Indian conditions to ensure protection against static electricity.
Bonding and earthing are different and to that effect you still have to adopt proper methods please.
Regards,
Kesava Pillai

From India, Kollam
dipil
713

Dear Sir
Thanks for your valuable reply... Could you please come with perfect answers to the quiries raised by you:
Here may I ask you few simple questions about the tanker earthing ?
Is its resistance ever measured ?
And if so what was the result?
What is the maximum resistance it can have for effectiveness ?
What depth we have to drive that rod to get that reading for effectiveness?
I have discussed the same with few electrical engineers but nobody was able to give a ready made answers and even after reffer given different reply's...
Hope to get positive reply from yourside.
Regards,
Dipil Kumar V

From India
shailesh.mann09
37

Dear All,
We are going to buy Earthing kit for Unloading / loading tankers for our plant. when it is fixed, I will definitely paste photographs.
Keshav Sir,
U have given really a good answer for all queries.
Thanks and keep us guiding.
Regards,
Shailesh

From India, Pune
Kesava Pillai
252

Dear Dipil,
Earth resistance measurement may vary from 0.5 to 20 ohms.
More than 20 ohms any where is not acceptable.
Mostly in Generating/Substation the earthing resistance will be too low and even possible to get a reading of 0.5 ohms.
Regarding earthing for tanker etc. for protection against ststic charge, it is already answered.
Regards,
Kesava Pillai

From India, Kollam
dipil
713

Dear Sir Thanks a lot for your reply... Let me share the same with my people and surely get back to you if anyone have any specific comments... Regards, Dipil Kumar V
From India
raghuvaran chakkaravarthy
497

Dear shailesh,
I am waiting for ur reply regarding Earthing kit for Unloading / loading tankers.Please share photographs with us.
keep sharing. . .
Thanks & Besafe
Raghu
"I am not totally waste / useless I am used as a bad example"

From United States, Fpo
Community Support and Knowledge-base on business, career and organisational prospects and issues - Register and Log In to CiteHR and post your query, download formats and be part of a fostered community of professionals.






Contact Us Privacy Policy Disclaimer Terms Of Service

All rights reserved @ 2024 CiteHR ®

All Copyright And Trademarks in Posts Held By Respective Owners.